- (d) $15\Omega$
Explanation:
Resistance of the two wire lines carrying power $=0.5\frac{\Omega}{\text{Km}}$
Total resistance $=(15+15)0.5=15\Omega$
- (c) 600kW
Explanation:
Line power loss = I2R
RMS current in the coil,
$\text{I}=\frac{\text{P}}{\text{V}_1}=\frac{800\times10^3}{4000}=200\text{A}$
$\therefore$ Power loss = (200)2 × 15 = 600kW
- (d) 1400kW
Explanation:
Assuming that the power loss is negligible due to the leakage of the current.
The total power supplied by the plant,
= 800kW + 600kW = 1400kW
- (b) 3000V
Explanation:
Voltage drop in the power line = IR
= 200 × 15 = 3000V
- (d) 7000V
Explanation:
Total voltage transmitted from the plant,
= 3000V + 4000V = 7000V